thick wall

Post by mohammmad » Thu Oct 08, 2020 9:33 pm

Hello,
When the thickness of the wall web is in the range of 80 cm to 120 cm, the core concrete of the web is surrounded by the surrounding concrete, how can we consider this effect?
As you know mander's equation can only use for boundary element and effect of A hoop and crosstie.

mhscott
Posts: 872
Joined: Tue Jul 06, 2004 3:38 pm
Location: Corvallis, Oregon USA
Contact:

Re: thick wall

Post by mhscott » Fri Oct 09, 2020 1:16 pm

There must be something in the literature about this. Or, depending on what you're doing, you can just ignore confinement in the web.

selimgunay
Posts: 913
Joined: Mon Sep 09, 2013 8:50 pm
Location: University of California, Berkeley

Re: thick wall

Post by selimgunay » Sat Oct 10, 2020 8:21 am

If you rely on the surrounding cover concrete for confinement, that may not be a good assumption as the confinement generally becomes active after spalling of concrete, which happens at early stages of damage